I could get an answer in seconds
Prediction: there will never be an answer.
Originally posted by backinblack
reply to post by exponent
Gotta love how you support Government views worldwide..
What a patriot you are..
Originally posted by exponent
I got linked to this thread by a friend and I must say I was engrossed by bsbray's increasing arrogance. It's been a while since I posted, but now he's beginning to believe he has authority to speak over engineering matters.
It's quite simple bsbray, the cardington tests do not prove what you want them to prove.
For a start, the test you're using are beam floored, over a very small span. As you (should) know, thermal expansion is a volumetric effect, and so in the direction of motion the length of the span is of high importance in determining the force applied.
As the span was so large, and the flooring was truss and therefore made of smaller elements in opposition, the sagging would have been much larger and quicker than at Cardington.
You also seem to be ignoring the floor restraints provided and the large difference once again with the Cardington tests.
All credit to Jon Cole though, he created a mechanism I didn't think was physically plausible
Originally posted by -PLB-
Originally posted by bsbray11
I could get an answer in seconds
Seconds become minutes. Minutes become hours. Hours become days.
Originally posted by bsbray11
You mean, like any other capable person, I have the ability to point out scientific studies and other facts. And that's different from anyone else posting here, such as yourself, how?
I already posted the conclusions from the Cardington tests themselves. It's hard to make up what the scientists who actually performed the study said about it.
You're only leading up to shooting yourself in the foot if you're about to argue that the expansion forces should have been even greater in the WTC Towers.
...
Exactly... so the expansion force would have been greater.
Someone screwed with PLB when he was a kid, so he doesn't know that larger forces produce larger deflections than smaller forces. Are you also going to ignore the fact that his own sources showed that the expansion forces are greater than any "pull" force such as what NIST claimed was responsible for the deflection? Where is the photographic evidence of widespread deflection from expansion?
It was only important that the beams were firmly restrained on both ends for the sagging to take place in the middle. This would have been the case at the WTC too. Now I guess you are going to ignorantly argue that sagging at the WTC couldn't have even taken place because the trusses were unrestrained on one end. How is that going to help your argument?
I'm surprised you're able to actually admit that.
Originally posted by exponent
Originally posted by bsbray11
You mean, like any other capable person, I have the ability to point out scientific studies and other facts. And that's different from anyone else posting here, such as yourself, how?
The difference is that when they disagree with you they lose credibility in your eyes.
I already posted the conclusions from the Cardington tests themselves. It's hard to make up what the scientists who actually performed the study said about it.
Indeed it is, but once you ignore enough information, you can start to form a weak chain with the remaining tenuous facts.
You're only leading up to shooting yourself in the foot if you're about to argue that the expansion forces should have been even greater in the WTC Towers.
...
Exactly... so the expansion force would have been greater.
Agreed.
Someone screwed with PLB when he was a kid, so he doesn't know that larger forces produce larger deflections than smaller forces. Are you also going to ignore the fact that his own sources showed that the expansion forces are greater than any "pull" force such as what NIST claimed was responsible for the deflection? Where is the photographic evidence of widespread deflection from expansion?
Different system, truss floors have a bottom chord in tension, and although a beam has a similar thing it is not a unique element. Plus of course the difference in construction and loading. It wouldn't be fair to make a direct comparison, only as a general concept.
It was only important that the beams were firmly restrained on both ends for the sagging to take place in the middle. This would have been the case at the WTC too. Now I guess you are going to ignorantly argue that sagging at the WTC couldn't have even taken place because the trusses were unrestrained on one end. How is that going to help your argument?
I'm not, but you have mentioned the dampers installed but without discussing the actual truss connectivity. It may be worth comparing how a truss connected to a typical column with how the beam connects in PLBs example (they're actually called different things too)
So, as you've been courteous to answer my questions, and I have been courteous to answer yours, here is my most important question:
Have you come up with a plausible mechanism to cause perimeter pull-in?
Originally posted by bsbray11
overly-complicated garbage
Originally posted by -PLB-
Originally posted by bsbray11
overly-complicated garbage
That is how real engineers solve problems
Originally posted by bsbray11
Well I'll still be here when you're reading to point out what information either I or the scientists involved with that study were ignoring, when they formed their conclusion and wrote it all out, like I just posted on the other page.
You realize this is the exact opposite direction of the force NIST hypothesized to initiate "collapse," right?
For all these differences you still can't tell me how it would mean a smaller force can cause more displacement than an even larger force. The differences are noted, and they're also apparently inconsequential to the point here, which is that the expansion forces are significantly larger than any "pull" force, and at even lower temperatures.
No. And I haven't seen any evidence of columns being "pulled in" on a large scale either.
Originally posted by exponent
No. And I haven't seen any evidence of columns being "pulled in" on a large scale either.
I'm not sure why exactly you deny these images, but here goes:
Originally posted by ANOK
How are those evidence of columns being pulled in?
Couldn't you be simply seeing the aluminum cladding bowed inwards?
Makes more sense than sagging trusses pulling in more massive columns. The fact that they're sagging due to heat expansion should show you that any movement would all be in the trusses themselves, not the more massive columns they're attached to.
'Equal opposite reactions', the trusses push against the columns, the columns push back with the same force.
The columns were more massive than the trusses, it doesn't require Einstein to tell us the outcome, Newton will do.
BTW, I hope you realise the cladding was not placed directly on the steel? There would have to be a gap due to galvanic corrosion, dissimilar metals can not be placed together. That is all you are seeing, the aluminum is pushed up against the columns from impact and heat.
Originally posted by exponent
Originally posted by bsbray11
Well I'll still be here when you're reading to point out what information either I or the scientists involved with that study were ignoring, when they formed their conclusion and wrote it all out, like I just posted on the other page.
Could you please link me to that? I had a look through your posts in this thread but there are 15 pages of them and I couldn't see it specifically.
The key findings of the project can be summarised as:
* The composite steel framed building tested exhibited inherently stable behaviour under the tested fire scenarios due to the highly redundant nature of the structural form.
* This behaviour is characterised by several thermo-mechanical phenomena, which interact. This complex interaction is highly dependent upon the structural layout and the thermal regime of the fire compartment considered.
The main objective of the project can be stated as:
`To understand and exploit the results of the large scale fire tests at Cardington so that rational design guidance can be developed for composite steel frameworks at the fire limit state'
This objective was achieved by:
* Developing rigorous, robust finite element models using state of the art, commercial finite element modelling programmes. These models were thoroughly validated using the results of the major Cardington fire tests.
* Developing properly validated, computationally efficient, simplified models to accurately predict the behaviour of multi-storey steel frame structures under fire conditions. These models were developed using both commercial and research finite element packages by an iterative process of comparison with rigorous models and experimental data.
* Developing different models of the same phenomena independently, in parallel to test model sensitivities and modelling assumptions.
* Developing methods of post-processing results so that the underlying structural mechanics can be more easily understood.
* Using the simplified models to conduct parametric studies to explore changes of structural behaviour.
* Checking the consistency of model results with the fundamental principles of structural mechanics by developing appropriate theory.
The Broadgate fire was introduced in Chapter 1 of this thesis. Structural damage caused by the fire included distortion of a number of trusses and universal beams and axial shortening of five columns by 100mm. The deflection of the trusses produced dishing of the floor of up to 600mm relative to the columns. The concrete floor slab separated from its metal decking in some areas but generally followed the level of its deflected supporting members. Despite large deflections, the structure behaved well and there was no collapse of any of the columns, beams or floors. [115]
The behaviour of the structure and the floor members showed that a steel frame designed to BS 5950 Part 8 is structurally safe when exposed to a severe fire. The study [115] carried out after the Broadgate fire showed that when fire affects only part of a structure (compartmentation) and when the framework acts as a total entity structural stability is improved.
Detailed studies of the material properties at high temperatures were carried out and it was concluded that apart from the concrete to the first floor no material showed significant loss of strength due to the fire. Detailed metallurgical investigations were carried out to asses the temperatures reached by the quenched and tempered bolts recovered from several of the beam to column connections in the areas of the fire which showed most damage. These indicated that the most severe temperatures achieved by the bolts during the fire or during manufacture were limited to 540°C. Similar evidence from a truss indicated that the member had been heated to around 600°C. The principles of BS5950 Part 8 would suggest that these members would transfer load to cooler parts of the structure until temperatures of about 700~800°C but the investigations suggest that the temperatures achieved did not exceed 600°C so an alternative explanation for the deformations observed was needed.
You realize this is the exact opposite direction of the force NIST hypothesized to initiate "collapse," right?
Yes? I don't see why you think that is a problem, NIST also did not as it is included in NCSTAR 1-6C
For all these differences you still can't tell me how it would mean a smaller force can cause more displacement than an even larger force. The differences are noted, and they're also apparently inconsequential to the point here, which is that the expansion forces are significantly larger than any "pull" force, and at even lower temperatures.
These forces are determined by different things, expansion is determined by temperature, wheras pull in is also determined by the floor loading. How can you say that the expansion forces would be lower in the WTC without analysis? Do you think it's a general rule?
I'm not sure why exactly you deny these images, but here goes
Originally posted by bsbray11
These were very thorough tests, as described:
...
At the end they list different ranges of temperatures and the different phases the structure goes through based on their research.
If only NIST had been this logical, straightforward, and thorough, we wouldn't even be having this discussion.
NIST included a lot of information that didn't agree well with their own hypothesis, and ignored even more, but I only find that as another reason for a real investigation.
First of all the expansion forces are greater than any "pull" forces, not "lower," so that was a typo I guess.
That's according to the only source posted so far, by PLB. I was going off memory from what I read of these reports, and they mentioned no significant "pulling" forces either.
If you want a specific analysis for the WTC, why didn't NIST do one? I can only imagine.
I don't see any reason why it should show that any "pull" forces should have been greater than the forces created by thermal expansion. Read those studies and you'll notice there is no evidence of steel itself being heated much beyond 700 C. The temperatures required to reverse expansion forces are 800 C and beyond.
NIST found no evidence of this, neither is there any evidence in these studies that it realistically happens. The fire itself is typically 800 C at most, excepting flashover conditions which are brief.
And the temperatures required for maximum thermal expansion forces are significantly less.
First of all, where is all the outward expanding we should be seeing, according to all the science posted on this thread already?
It happens at greater forces and at lower temperatures, meaning it should be more visible and sooner. So where is it?
Secondly, what you are actually looking at, in the first photo especially, is predominantly aluminum cladding, not the actual exterior columns. So when you disregard all that cladding jutting out at odd angles and badly mangled, look at what's left. They are not showing you enough perimeter column deflection to seriously endanger the entire floor even by their own admission that the perimeter columns retained 4/5 of their reserve capacity on the morning of 9/11.
That equates to a safety factor of 5 and if you haven't seen this already then just say the word and I'll go dig up my old thread where I showcased the NIST excerpt confirming this.
Also heat fields distort light and this is an unfortunate fact. I'm assuming all the deflection they actually show is really there, and it's still not enough to cause a whole floor to collapse given that the perimeter columns there had a safety factor of 5. But in reality what NIST is labeling as buckled columns may be light distorted by the changes in air temperature between the fire and the photographer.
But still more importantly to me, and ignoring the aluminum cladding and the effects of heat on light, and assuming the buckling they show is all there, their explanation also still defies all the science posted here so far, that would indicate more significant deflections outwards should have been observed, and sooner.
Lastly, also assuming the buckling they show is really all there, they don't rule out the possibility that it was caused by any other mechanism, because they considered no other mechanisms.
So those reasons together make up one summary as to why those photographs are inadequate for validating NIST's hypothesis.
Originally posted by exponent
Yes if only NIST had performed real-world tests or examined connections or trusses or columns or hold on one second. They did actually do all of this, so once again you are trying to sneak in some unwarranted criticism. No real shock there because they represent your opponents but a good example of bias again.
I was hoping you'd have some more specific conclusion, but all I wanted to check was that you were talking about beams attached via shear connectors to the columns. These behave quite differently to the trusses would in the towers.
NIST included a lot of information that didn't agree well with their own hypothesis, and ignored even more, but I only find that as another reason for a real investigation.
You find them including information that didn't agree well to be a reason for more investigation? Strange approach.
That's according to the only source posted so far, by PLB. I was going off memory from what I read of these reports, and they mentioned no significant "pulling" forces either.
Well, there's no denying that there will be pulling forces, once the beams or trusses have sagged enough that they become unrestrained
The question was: do you think that it is a general rule that the pushing forces are always higher than the pulling forces. Can you demonstrate this?
If you want a specific analysis for the WTC, why didn't NIST do one? I can only imagine.
They did.
I don't see any reason why it should show that any "pull" forces should have been greater than the forces created by thermal expansion. Read those studies and you'll notice there is no evidence of steel itself being heated much beyond 700 C. The temperatures required to reverse expansion forces are 800 C and beyond.
So if we replace a short span beam with a 45 foot truss, then fire a few of them, what will occur? Please show us how you work it out.
NIST found no evidence of this, neither is there any evidence in these studies that it realistically happens. The fire itself is typically 800 C at most, excepting flashover conditions which are brief.
Woah woah woah. Just a minute ago you didn't know if NIST did the tests, now you know they did and their conclusions? I think not.
Please read their experimental tests of office compartments so you can stop imagining temperatures you prefer and believing that it's true.
The typical maximum temperature of these fires was over 1000C, I have no clue where you get 800C from.
And the temperatures required for maximum thermal expansion forces are significantly less.
Uh, so at anything above that the pull in forces will develop, although you just said they couldn't. Confusing.
First of all, where is all the outward expanding we should be seeing, according to all the science posted on this thread already?
It happens at greater forces and at lower temperatures, meaning it should be more visible and sooner. So where is it?
It's restrained, it actually helps to increase the sag of the trusses by stopping them expanding.
Secondly, what you are actually looking at, in the first photo especially, is predominantly aluminum cladding, not the actual exterior columns. So when you disregard all that cladding jutting out at odd angles and badly mangled, look at what's left. They are not showing you enough perimeter column deflection to seriously endanger the entire floor even by their own admission that the perimeter columns retained 4/5 of their reserve capacity on the morning of 9/11.
This is a concentrated paragraph of rubbish. You're not looking predominantly at the aluminium cladding, the cladding did as it was called, it clad the steel, as in it surrounded it on 3 sides and matched the profile. There is no reason nor mechanism to believe that the cladding is responsible for the deformation and not the steel placed literally inches underneath it.
Secondly, no they didn't retain 4/5th of their reserve capacity. That was live load and as with all columns, severely deflecting them diminishes any load carrying capacity extremely quickly.
After reaching the yield strength, structural steel components continue to have significant reserve capacity, thus allowing for load redistribution to other components that are still in the elastic range.
On September 11, the towers were subjected to in-service live loads, which are considered to be approximately 25 percent of the design live loads.
On September 11, the wind loads were minimal, thus allowing significantly more reserve capacity for the exterior walls (demand on exterior columns was about 1/5 their capacity).
That equates to a safety factor of 5 and if you haven't seen this already then just say the word and I'll go dig up my old thread where I showcased the NIST excerpt confirming this.
Go for it, see if you can find the difference between live and dead load while you're at it.
As you're so fond of diagrams, please draw this out so we can visually appreciate your argument.
The refraction caused by temperature differences is easy to calculate.
Why if only you'd actually read the science available, rather than just assuming you understand the behaviour of this immensely complex structure. You'd know that the initial phases occurred before significant truss -> perimeter disconnection, and that the restraining effects of several hundred trusses were enough to stop serious outward deflection, although some undoubtedly occurred. The inward deflection comes later, and is the result of the damage towards large numbers of trusses.
Lastly, also assuming the buckling they show is really all there, they don't rule out the possibility that it was caused by any other mechanism, because they considered no other mechanisms.
You're right, they didn't consider any other mechanism. Funny that. I've been asking you for years to come up with one, and you still haven't, so what exactly do you expect NIST to test?
So those reasons together make up one summary as to why those photographs are inadequate for validating NIST's hypothesis.
Right, you don't like their conclusions, so you grasp at straws to deny them. I mean come on, 'cladding damage'? You're a fool to yourself if you believe that.
There is fairly broad agreement in the fire science community that flashover is reached when the average upper gas temperature in the room exceeds about 600°C. Prior to that point, no generalizations should be made: There will be zones of 900°C flame temperatures, but wide spatial variations will be seen.
Of interest is the maximum value which is fairly regularly found. This value turns out to be around 1200°C, although a typical post-flashover room fire will more commonly be 900~1000°C. The time-temperature curve for the standard fire endurance test, ASTM E 119 [13] goes up to 1260°C, but this is reached only in 8 hr. In actual fact, no jurisdiction demands fire endurance periods for over 4 hr, at which point the curve only reaches 1093°C.
It is common to find that investigators assume that an object next to a flame of a certain temperature will also be of that same temperature. This is, of course, untrue. If a flame is exchanging heat with a object which was initially at room temperature, it will take a finite amount of time for that object to rise to a temperature which is 'close' to that of the flame. Exactly how long it will take for it to rise to a certain value is the subject for the study of heat transfer. Heat transfer is usually presented to engineering students over several semesters of university classes, so it should be clear that simple rules-of-thumb would not be expected. Here, we will merely point out that the rate at which target objects heat up is largely governed by their thermal conductivity, density, and size. Small, low-density, low-conductivity objects will heat up much faster than massive, heavy-weight ones.