Originally posted by Lumos
2) This depends a lot on atmospheric conditions. Generally, the better the oxygen supply, the hotter. Under standard atmospheric conditions, around 800°C can be attained.
4.) Just how were the towers constructed? Was the support mainly in the steel columns? Or was the support spread throughout the building? (any available blue-prints would be greatly appreciated)
5.) Upon learning more about how the towers were constructed, what would be the maximum load that any one portion of the load-bearing structure could hold?
The factor of safety is based upon the dead load (building materials) of the building and the intended live load (people, office furniture, and similar). The dead load of a floor was 1,818 tons. The floor area was rated 40-150 psf (1.9-7.18 kPa), depending on what the area was going to be used for. Higher load ratings generally were for areas that would support larger than normal loads such as mechanical equipment. Below are floor load estimates based on a review of WTC data contained in a 2005 NIST report. This report contained select scanned images of original WTC specification documents. Because of contradictions in the NIST final report this paper relied on the original WTC specification documents. Data was incomplete so inferences had to be made. The load rating for columns in the perimeter area was 50 psf. The load rating for the core area was up to 100 psf. This comes out to be an estimated 75 psf average for an office floor. The load ratings for floors 110-94 average out to be about 82 psf (3.9 kPa) per floor. On average, a floor's design live load was 1,488 tons. The estimated total weight of a floor, dead load plus live load, is 3,306 tons. Add the factor of safety and the building structure could handle multiple times this load. It is estimated that the average factor of safety for a floor was 3.35. This means a floor could handle a total of 11,075 tons before failing. To visualize, imagine 5,500 2-ton cars stacked in a square about 1/3 of a city block.
6.) Besides the steel frames, what would be the maximum temperatures that any other loading bearing structures could withstand?
7.) What else was present in the towers where the planes hit besides steel and jet fuel?
I believe that number four is the most important. How the weight of the building was supported is very important. If threads such as this already exist, feel free to point me in the right direction and close this one.
Originally posted by Lumos
Craig, if that were true, how do all those nonfatal highrise fires fit in?
Reading this report gave me a headache! The buildings mentioned and the subsequent tests were conducted on buildings under construction, not on buildings completed and under full occupancy load. The load on the WTC buildings was much greater than on the buildings sited in the report. Also, metal weakens over time due to metal fatigue. We need to take into consideration 30 years of stresses from weight, wind flex, etc. on the WTC. Also, these buildings were not full of carpeting, sheet rock, office furniture, wall vinyl, office supplies, etc. that basically became "wicks"... In the WTC these items became soaked in jet fuel and then burned unchecked.
Originally posted by LumosWhat about the Cardington fire tests?
Not quite sure what you mean by this. Do you mean that they found steel beams at that temperature in the debris after the collapse? Heating steel to these temperatures would not melt it or cause it to glow, however, that heat would certainly weaken the steel.
Originally posted by LumosWhat about NIST's published steel analysis finding few members above 250°C and no members above 650°C?
What about them? Many of them jumped to avoid the searing heat they were faced with. They could not reach the exit stairs because the raging fires were blocking their escape routes, so they preferred to die by jumping than die by burning.
Originally posted by LumosWhat about the pictures of people within the impact holes?
What about them? What floor where they on? There were small pockets of fire reported as low as the 65th floor in the south tower that I know of; maybe someone can provide more accurate information as to what the lowest floor fire was reported on through the FDNY transcripts that have been published. Anyone who was there that day knows that the firefighters never made it up to the actual floors where the fires were intensely burning. Not one drop of water was put on the fires by FDNY.
Originally posted by LumosWhat about the firemen up in the south tower reporting "isolated pockets of fire" that they should be able "to knock down with 2 lines"?
One possible cause and one definite cause. Possible: The buildings were designed to flex and sway a certain amount for wind. Is it possible that the impact of a large airplane at full speed caused the building to flex to a greater degree than it was designed for? Definite: The debris falling from the building (plane parts, building parts, glass, bodies, office furniture, etc.) didn't just fall 90 stories and hit the ground gently. They fell and literally exploded when they hit the ground. Shrapnel from these falling objects broke many windows. Police officers also used their weapons to shoot out many of the glass window panes to facilitate evacuation. Also, several elevators had their cables completely severed by the impact and their safety brakes failed, causing them to crash into the bottom of their shafts. The bottom of their shafts in some cases were at the lobby level, blowing debris out of the shaft into the lobby.
Originally posted by LumosWhat about the apparent damage to the lobby?
WTC 7 had a large quantity of diesel fuel stored in it for the emergency generator in the Office of Emergency Management's generator. This fuel burned unchecked for many hours, again with no firefighting.
Originally posted by LumosWhat about WTC7?
Originally posted by craig732
Surrounding steal in concrete is what protects most high-rise buildings from collapsing due to weakened steel.
Steel in such a building is sprayed with an insulation to protect it from heat. It is speculated that much of the insulation was blown off the steel during the initial explosion, and that the intense fires exceeded the remaining insulation's fire rating.
As for the people that say jet fuel only burns at such-and-such a temperature, you need to take into consideration that it wasn't just jet fuel burning. It was sheet rock, doors, chairs, office furniture, carpeting, etc. soaked in jet fuel that was burning.
Originally posted by aggroskater
1.) What is jet fuel composed of?
Originally posted by Lumos
1) Jet fuel consists of hydrocarbons in the range of c10h22-c16h34
Originally posted by aggroskater
2.) What is the maximum temperature that jet fuel can attain?
Originally posted by Lumos2) This depends a lot on atmospheric conditions. Generally, the better the oxygen supply, the hotter. Under standard atmospheric conditions, around 800°C can be attained.
Originally posted by bsbray11
I think 800°C is more of the upper range of hydrocarbon fires, but I could be mistaken. I honestly haven't read much on the nature of your average hydrocarbon fires.
Either way, they won't go much beyond 800°C, and steel is a good heat sink. Tons upon tons upon tons of steel, even moreso. 800°C of fire, spread out amongst literally tons of steel, isn't going to make for very hot steel.
Thus, you saw no glowing of steel at either WTC Tower on 9/11, when steel will begin giving off photons at somewhere around 400°C. Still won't lose critical strength until heated to around 600°C, and the WTC Towers needed to lose about 60% more integrity than the initial impacts caused for any given floor to collapse. So, even in ideal conditions, it would be damned near impossible for the fires in the WTC towers to have sufficiently weakened the steel.
Originally posted by bsbray11
Thus, you saw no glowing of steel at either WTC Tower on 9/11, when steel will begin giving off photons at somewhere around 400°C. Still won't lose critical strength until heated to around 600°C, and the WTC Towers needed to lose about 60% more integrity than the initial impacts caused for any given floor to collapse. So, even in ideal conditions, it would be damned near impossible for the fires in the WTC towers to have sufficiently weakened the steel.
Originally posted by aggroskater
4.) Just how were the towers constructed? Was the support mainly in the steel columns? Or was the support spread throughout the building? (any available blue-prints would be greatly appreciated)
Originally posted by Lumos
4) 47 core columns bearing approx. 60% gravitic load, 220 (or so) perimeter columns bearing the remaining 40%.
Originally posted by bsbray11
The buildings consisted of perimeter and core columns, which were linked by trusses between floors. All of that was made of steel. The core columns probably held the good majority of the gravity load; I've seen it 50/50, and 60/40, and it was Howard saying 50/50 so I'm betting that he's skewing it to make the buckling thing more credible. I think the 60/40 thing was given in a NIST presentation, and it came to me via a paper by Wayne Trumpman. Since NIST was giving the 60/40 figure, don't bet on that being entirely accurate, either.
The core columns were in the middle of the buildings, and there were offices built within them. The stairwells were within the core structure, if I remember correctly, and the elevators. The core columns could likely hold some lateral loads as well as much vertical load, so theoretically, the core structures would have been able to stand perfectly well without the perimeter columns and trusses, but would probably be much more vulnerable to wind (such loads were taken by the perimeter columns and trusses). In a video of the collapse of WTC1 from Hoboken, you can see parts of the core of WTC still standing after all of the perimeter columns and trusses have fallen away.
There were concrete slabs, about 4 inches thick, between each floor.
The construction drawings of the towers are classified and are not publicly available.
Originally posted by aggroskater
5.) Upon learning more about how the towers were constructed, what would be the maximum load that any one portion of the load-bearing structure could hold?
Originally posted by Lumos
5) Impossible to answer. Safety standards seem to dictate overload factors of 3-6, i.e. the actual load may only be 1/3-1/6 of the maximum certified load.
Originally posted by bsbray11
5.) Upon learning more about how the towers were constructed, what would be the maximum load that any one portion of the load-bearing structure could hold?
Ok, first of all let me say that this may be horribly inaccurate. We don't have the construction papers, so we don't know this for sure.
But Wayne Trumpman's paper, which you can find here, claims that each floor could withstand, on average, 11,075 tons of load before failing. This number would likely widely vary, between stronger columns were used in the bottoms of the towers, and the higher floors were lighter and not as strong.
The specific part of Trumpman's paper that I'm referencing says the following:
(edited, see above – HR)
Originally posted by aggroskater
6.) Besides the steel frames, what would be the maximum temperatures that any other loading bearing structures could withstand?
Originally posted by Lumos
6) Probably irrelevant, as the loadbearing structure apparently was steel only. Rumour has it that the core sported concrete, but we don't know.
Originally posted by bsbray11
This depends upon how much weight is being supported, and how much strength would be lost at what temperatures.
At around 600°C, steel loses about half its integrity. At around 250°C, steel has lost none of its integrity, or at least so little that it's not even notable. The steel NIST tested shows no steel heated above 250°C; that is to say, 250°C was around the max that NIST detected. You can rest assured that no steel was heated much above 400°C, as it would have started glowing and would have been visible in broad daylight.
Originally posted by aggroskater
7.) What else was present in the towers where the planes hit besides steel and jet fuel?
Originally posted by Lumos
7) Offices?
Originally posted by bsbray11
Some paper; plastic. Concrete, asbestos, and Gypsum, I think. People.
August 31, 2003 -- The fiery hell that raged inside the World Trade Center on 9/11 has been recreated in a test that highlights how today's office space can be dangerously flammable, as these dramatic pictures show.
Using a cubicle based on the offices of insurance firm Marsh & McLennan - a north tower tenant that lost 295 employees - federal fire experts conclude it was more likely the heat of burning office materials brought down the tower, rather than jet-fuel-fed flames.
This test, conducted by National Institute of Standards and Technology last month, showed the fuel from the plane that crashed into the tower burned out quickly - but the fire it created grew in intensity by up to another 300 degrees as it consumed office products and structures.
The computers, cubicle walls, furniture, files and paper - recreated on detailed information supplied by the insurance company on the exact materials used in their offices - blazed at temperatures that reached 1,200 degrees, the NIST test found.
The test fire burned for 33 minutes before the 386 pounds of material were consumed and reduced mostly to ash and gases.
Originally posted by craig732
Originally posted by Lumos
Craig, if that were true, how do all those nonfatal highrise fires fit in?
I cannot speak for the other buildings, but the Meridian Plaza Building in Philadelphia is constructed of concrete and granite encased steel, and the One New York Plaza building was constructed of concrete encased steel. These buildings were not of the same design as the WTC buildings. Also, fire needs three things to burn: oxygen, fuel, and heat. In normal building fires, the sprinkler systems go a long way to control the spread of the fire by wetting the fuel and keeping the temperatue of the fuel cooler than if it is dry. In the case of the WTC, most of the sprinklers failed due to the sprinkler risers being severed by the initial impacts.
Floor construction. The use of a four inch concrete floor over corrugated steel I beams has failed at every multiple alarm fire in New York City. Floor steel beam supports sag, warp and twist. The four inch concrete floor above sags with the steel cracks and heaves. Smoke and flames spread to the floor above. Floor beams and concrete floor surface must be replaced after every serious fire. This started at the 1970s fire in 1 New York Plaza, where 130 steel floor beams were replaced and 20,000 square feet of concrete floor was removed.
Originally posted by HowardRoark
Now an interesting thing to consider is this:
We are all familiar with the use of the term watt in relation to energy.
Watts are defined as joules/second.
Thus a 1000 watt fire released 1000 joules per second.
How many watts of energy would be released by 1,000 gallons of jet fuel burning up in 5 minutes?
1,000 gallons of jet fuel = about 3066 kg.
thus the combustion of 1,000 gallons of jet fuel in 5 minutes will release around 437 megawatts of energy.
Worth thinking about.
In any case. Stating that jet fuel can only burn at such and such temperature is incorrect.
Even the temperature of a candle flame can exceed 1000 degrees C.
Originally posted by HowardRoark
The melting point of aluminum is 660 Degrees C.
At this corner of the building, the fire apparently got pretty hot.
Originally posted by HowardRoark
The general design is what is called a “framed tube” construction. The WTC towers were not the only structures to use this construction method, but they were one of the first.
The exterior columns were designed to withstand all of the lateral loads and approximately 50 percent of the gravity loads.
The core was not designed to resist lateral loads, but it supported 50 % of the gravity loads.
The designs of the buildings are not classified. Enough information is available for any reasonably competent engineer to understand the structural system. The NIST reports have numerous design documents in the appendices.
Originally posted by HowardRoark
Trumpman's analysis is fraught with errors.
In addition, I have yet to see any indications of his credibility. i.e. is he an engineer?
In any case, the issue here is not all that simple, since you have to try and calculate the affect on the impact and fire damage on the building, and how loads were redistributed as the structural integrity of various portions of the building was compromised.
Originally posted by HowardRoark
The NIST report did not show that none of the steel was heated above 250 degrees. It stated that the two pieces of steel recovered from the core region on the impact floors, were not heated above those temperatures.
Observations of paint cracking due to thermal expansion. Of the more than 170 areas examined on 16 perimeter column panels, only three columns had evidence that the steel reached temperatures above 250 ºC: east face, floor 98, inner web; east face, floor 92, inner web; and north face, floor 98, floor truss connector. Only two core column specimens had sufficient paint remaining to make such an analysis, and their temperatures did not reach 250 ºC (p. 90).
There is clear photographic evidence that major damage to the floor slabs occurred in the areas directly impacted by the aircraft.
There is evidence that the fireproofing applied to the trusses under the slabs was generally in poor condition prior to 9/11.
Originally posted by bsbray11
Originally posted by HowardRoark
The NIST report did not show that none of the steel was heated above 250 degrees. It stated that the two pieces of steel recovered from the core region on the impact floors, were not heated above those temperatures.
Damn, Howard! You're just going all out with deception today. Must be all these people suddenly dropping the official line or something.
From the NIST Report (emphasis mine):
Observations of paint cracking due to thermal expansion. Of the more than 170 areas examined on 16 perimeter column panels, only three columns had evidence that the steel reached temperatures above 250 ºC: east face, floor 98, inner web; east face, floor 92, inner web; and north face, floor 98, floor truss connector. Only two core column specimens had sufficient paint remaining to make such an analysis, and their temperatures did not reach 250 ºC (p. 90).
Do you know what that means? They tested much more than just two samples!