Got a major fault alarm notification on a 200 kVA UPS going crazy, in a major data center. All sorts of alarms going off. Panels over-temp, things over amp...nothing makes sense.
Okay...some background. For whatever reason this is a 208V 3p input UPS, stepped down from a 277/480 V 3p 75 kVA transformer. In the middle we have an Automatic Transfer Switch and a twin 600kW generator setup. Okay, solid set up. Input voltage to the rectifier is 208 VAC 3p, to the batteries.
Something is going "BAD" wrong! Lugs in the service panel are getting hot (200+ degrees F). UPS is showing faults galore.
We get called. Crazy voltages on the neutral. Okay, let's start the checkout and see if you can figure it out....
Here's what we find. I go in and check the rectifier voltages and get the following (yes, I know it's crazy).
A-Ground = 208
B-Ground = 208
C-Ground = 208
All good, right?
A-B = 480
B-C = 480
AND...
A-C = 208 !!!
What happened?
This was measured on the output side of the maintenance bypass transformer!
Temps are going up in the panels. Something is going haywire. Shutting down the bypass and the distribution transformers means the data center goes dark (not an option!). Time pressure is ON!
What is the problem??
originally posted by: Flyingclaydisk
a reply to: Thenail
My apologies for the delay in responding! Got pulled away on something else, then life.
Somethings loose ... Check your c phase tightness ... Do you want me to come there and fix it for you lol .
BINGO!! We have a winner!
Electrician who made up the Distribution panel back in an electrical room about 400 yards away didn't get the C phase let torqued down properly. Conductor came loose from the lug and sprang over and made contact with the A phase, hence the readings.
I never would have believed it unless I saw it.
As it turned out it was another Master Electrician (such as yourself) who deduced the same thing. "Only way this could even be possible is if...". At the same time, one of the lugs in the service panel serving the transformer was also loose, hence the heat issue. The heat issue likely contributed to the fault back at the Distribution Panel also.
That electrician is no longer with the electrical firm who did the work.
Very good! Excellent deduction!
ETA - So you really are "that good"!
originally posted by: Thenail
a reply to: randomtangentsrme
Ok
A three phase panel . You know The big panel say in an office building that houses all the breakers that you can use to turn the power on and off .
It has 3 incoming Hot wires and a neutral and a grounding wire . The 3 hots are black red and blue . They each have 120 volts to ground and 208 volts between them phase to phase . Hence the 120/208 3 phase power . Now if you have a 208 volt three phase piece of equipment you’ll need a black red and blue and green grounding wire typically sometimes a neutral but not needed . This is the 4the time I’ve posted something like this now you understand .
With 208, you are taking 2 hot legs, the white neutral leg, and the green grounding leg.